CXG4D: How set wired input NC for water leak detector TK102

Posted: Fri Feb 12, 2010 1:04 pm
by admin
The diagram shows TK102 water leak detector

Image

Then connecting the NC wires (blue and yellow) to alarm input liked this.

Image

By default it is Closed Circuit Triggered and this water leak detector is NO, therefore, you need to change the input zone from NC to NO by default, then when there is water leakage, the poles touching ground closed, it will alarm.

the SMS for this example, as the NC connecting to second Wired Input

123456#67#1#Wired zone 1#1#

66 is the 1st wired zone, so 67, 68, 69 and 70 are 2nd, 3rd, 4th, 5th zone.
1st 1 is activate this zone
2nd 1 is open circuit alarm ( 0 is closed circuit alarm )